## [Hot Wire Thermal Circuit Breakers](https://www.mechprod.com/blog-old/bid/294569/Hot-Wire-Thermal-Circuit-Breakers)

- [Tweet](https://twitter.com/share)

In a hot wire circuit breaker a wire of length x0 at reference temperature T0 will expand by length Δx=x0atΔT for temperature rise ΔT.  This temperature rise, as in a fuse element, can be generated by the I2R loss in the wire itself. 

 ![describe the image](https://www.mechprod.com/hs-fs/file-56757851-jpg/images/p69fig313.jpg?width=500&height=304&name=p69fig313.jpg)

 

If a given wire extension Δxtrip trips a latch mechanism, which releases a contact separation mechanism (see Figure 3.13), the needed temperature rise within the wire at the detection threshold is then ![describe the image](https://www.mechprod.com/hs-fs/file-56757586-jpg/images/p68equation38.jpg?width=150&height=47&name=p68equation38.jpg)

We now have a situation exactly analogous to that of the detection mechanism in a fuse.  The exception is that we need only raise the element temperature to the value given by (3.8), not to the melting point.  The thermal circuit analysis Equations 3.1 through 3.4, with suitable notation changes, also apply to the hot wire thermal circuit

![describe the image](https://www.mechprod.com/hs-fs/file-57868185-jpg/images/p60equation31.jpg?width=199&height=106&name=p60equation31.jpg)

 ![describe the image](https://www.mechprod.com/hs-fs/file-57868118-jpg/images/p60equation32.jpg?width=175&height=50&name=p60equation32.jpg)

 

 ![describe the image](https://www.mechprod.com/hs-fs/file-57868074-jpg/images/p60equation33.jpg?width=150&height=49&name=p60equation33.jpg)

![describe the image](https://www.mechprod.com/hs-fs/file-57867924-jpg/images/p60equation34.jpg?width=200&height=143&name=p60equation34.jpg)

We define

Ar = the wire temperature coefficient of resistivity,

Ro = the wire resistance at the reference temperature,

Rt  = the thermal resistance of the wire to the surroundings,

Ith = the steady-state DC current which will raise the temperature by ΔTth (i.e. the long trip time current),

k  = the wire resistance temperature sensitivity factor = arIth2RoRt  and Ct = the wire thermal capacity.

Thus, just as in Equation 3.4 for a fuse, we have for the hot wire temperature rise ΔT, and for any current I (t) ![describe the image](https://www.mechprod.com/hs-fs/file-56757464-jpg/images/p69equation39.jpg?width=248&height=53&name=p69equation39.jpg)

where![](https://www.mechprod.com/hs-fs/hubfs/blog-image-uploads/blog-bid-294569-hot-wire-thermal-circuit-breakers-img-1.png?width=15&height=22&name=blog-bid-294569-hot-wire-thermal-circuit-breakers-img-1.png) is the wire thermal time constant![describe the image](https://www.mechprod.com/hs-fs/file-56757656-jpg/images/p69equation310.jpg?width=98&height=37&name=p69equation310.jpg)

As an example, consider the use of an 80% Nickel – 20% Chromium alloy wire, which has the trade name Nichrome V.  This alloy has the average properties:

Reference resistivity:  ϱo = 108 x 10-6 Ω-cm (20o)

Coefficient of resistivity:  αr = 1.1 x 10-4/0C (20-500o C)

Coefficient of expansion:  αt = 1.7 x 10-5/oC (10-1000oC)

Specific heat:  Cp = 435 J/kgoC.

Assume that the relative extension of the wire at the trip threshold Δxtrip/xo is to be 0.5%.  Thus, by (3.8)

 ![describe the image](https://www.mechprod.com/hs-fs/file-56757622-jpg/images/p70equation6.jpg?width=150&height=36&name=p70equation6.jpg)

If we choose #30 wire (American wire gauge) we have the following data from the manufacturer:

Wire diameter:  0.010 in

Resistance at reference temp:  Ro = 6.500 Ω/ft(20oC)

Mass:  2.86 x 10-4 lbm/ft

Long time heating current for horizontal wire in air: ![describe the image](https://www.mechprod.com/hs-fs/file-56757713-jpg/images/p70equation9.jpg?width=150&height=75&name=p70equation9.jpg)

The wire thermal capacity per foot is then

 ![describe the image](https://www.mechprod.com/hs-fs/file-56757756-jpg/images/p70equation10.jpg?width=250&height=69&name=p70equation10.jpg)

If we use the free air heating-temperature data at I (RMS) = 1.21 A, we have for the wire resistance  R

 ![describe the image](https://www.mechprod.com/hs-fs/file-56758048-jpg/images/p70equation11.jpg?width=200&height=80&name=p70equation11.jpg)

Thus

 ![describe the image](https://www.mechprod.com/hs-fs/file-56758217-jpg/images/p70equation12.jpg?width=200&height=33&name=p70equation12.jpg)

The free air thermal time constant is then ![describe the image](https://www.mechprod.com/hs-fs/file-56757786-jpg/images/p70equation13.jpg?width=250&height=27&name=p70equation13.jpg)

The long time threshold current is

 ![describe the image](https://www.mechprod.com/hs-fs/file-56757875-jpg/images/p70equation14.jpg?width=200&height=65&name=p70equation14.jpg)

And the wire resistance temperature sensitivity factor k is

 ![describe the image](https://www.mechprod.com/hs-fs/file-56758004-jpg/images/p70equation15.jpg?width=200&height=77&name=p70equation15.jpg)

We can now, as we did for the equivalent fuse link, solve for the time it takes for the wire to reach its threshold temperature as a function of current.  These solutions are given in Figure 3.14.

 ![describe the image](https://www.mechprod.com/hs-fs/file-56758089-jpg/images/p71fig314.jpg?width=500&height=323&name=p71fig314.jpg)

Note that for Nichrome V the resistance temperature sensitivity factor is so low that we can, as a fair approximation, neglect the k multiplied term in (3.9) and solve the resulting equation analytically as ![describe the image](https://www.mechprod.com/hs-fs/file-56757905-jpg/images/p70equation16.jpg?width=150&height=52&name=p70equation16.jpg)

The time to reach the threshold temperature rise td is then given by

 ![describe the image](https://www.mechprod.com/hs-fs/file-56758141-jpg/images/p71equation312.jpg?width=150&height=49&name=p71equation312.jpg)

Which, for long (i/Ith)2, reduces to ![describe the image](https://www.mechprod.com/hs-fs/file-56757968-jpg/images/p71equation313.jpg?width=100&height=52&name=p71equation313.jpg)

 

 0 Comments [Click here to read/write comments](https://www.mechprod.com/blog-old/bid/294569/Hot-Wire-Thermal-Circuit-Breakers#comments-listing)

 Tags: [Temperature Rise](https://www.mechprod.com/blog-old/topic/temperature-rise), [Thermal Resistance](https://www.mechprod.com/blog-old/topic/thermal-resistance), [Nichrome V](https://www.mechprod.com/blog-old/topic/nichrome-v)

[All posts](https://www.mechprod.com/blog-old/all)

### Follow us!

<https://www.instagram.com/mp_circuit_breakers/><https://www.facebook.com/255072361223049><https://www.linkedin.com/company/991054><https://twitter.com/mechproducts>

### Subscribe by Email

### Latest Posts

### Posts by Month

- [May 2012 (4)](https://www.mechprod.com/blog-old/archive/2012/05)
- [July 2012 (3)](https://www.mechprod.com/blog-old/archive/2012/07)
- [April 2013 (3)](https://www.mechprod.com/blog-old/archive/2013/04)

**Mechanical Products**

**Count on MP for your thermal circuit breaker needs**

Tel: 630.953.4100  |  Fax: 630.953.4110  |  Email: [helpme@mechprod.com](mailto:helpme@mechprod.com)  
**www.mechprod.com**